node-red-contrib-waterkotte 0.1.5
Node-RED node for the Waterkotte heat pump (EcoTouch / IDAL CGI). Reads multiple tags in a single request, manages login token automatically.
Node-RED node for the Waterkotte heat pump (EcoTouch / IDAL CGI interface — accessible at port 80 on the local LAN, e.g. on the EcoTouch wall display).
Reads multiple tags in a single HTTP request, manages the login token automatically (re-login on 401), exposes scaled values and decoded status registers as a clean msg.payload object.
⚠ Breaking change in 0.1.5 —
status_*field names changed. Up to 0.1.4 theI51status register was decoded with bit numbers counted from 1, which shifted every bit by one (e.g. the alarm bit appeared asstatus_cooling_valve) and listed an EVU bit that is not part ofI51. Since 0.1.5 bits are counted from 0 (as in openHAB's EcoTouch binding) and the fields are renamed — see Status register I51. Old fieldsstatus_pump,status_evu,status_cooling_valveandstatus_water_valveno longer exist;status_compressornow carries the real compressor bit. EVU now comes fromI53asinterruption_flags_evu. Custombitsmaps are counted from 0 as well — subtract 1 from every bit number of an existing 0.1.4 map to keep its meaning.status._rawandinterruptionsare unchanged.
Why
The vendor offers no official Node-RED integration. Hand-built flows typically chain a dozen or more http request nodes, parse responses with custom function nodes, juggle the cookie-based IDALToken manually and break silently when the token expires. This package replaces all of that with two nodes.
In Node-RED → Manage palette → Install → search waterkotte.
Or from the command line:
npm install node-red-contrib-waterkotte
Quick start
- Drop a waterkotte read node onto a flow.
- Create a new waterkotte-config with host (e.g.
192.168.3.90), username and password (default on most installations:waterkotte/waterkotte). - Pick Tag-Preset → All common tags and a poll interval (e.g.
60seconds). - Wire the output into a debug node — you will see something like:
"temp_outdoor": 12.4,
"temp_outdoor_1h": 12.1,
"temp_outdoor_24h": 11.8,
"temp_return_set": 30.5,
"temp_return": 30.2,
"temp_flow": 33.1,
"temp_water": 48.6,
"heating_return": 30.4,
"heating_set": 30.5,
"percent_heat_circ_pump": 65,
"percent_compressor": 42,
"status_source_pump": 1,
"status_heating_pump": 1,
"status_evd": 1,
"status_compressor": 1,
"status_compressor2": 0,
"status_heater": 0,
"status_alarm": 0,
"status_cooling": 0,
"status_water": 0,
"status_pool": 0,
"status_solar": 0,
"status_cooling_4way": 0,
"interruptions": 0,
"interruption_flags_evu": 0
All values from one atomic round-trip — perfect for a single InfluxDB write.
Built-in tag preset
| Tag | Field | Unit | Description |
| A1 | temp_outdoor |
°C | Außentemperatur aktuell |
| A2 | temp_outdoor_1h |
°C | Außentemperatur 1h Mittel |
| A3 | temp_outdoor_24h |
°C | Außentemperatur 24h Mittel |
| A10 | temp_return_set |
°C | Rücklauf Soll |
| A11 | temp_return |
°C | Rücklauf |
| A12 | temp_flow |
°C | Vorlauf |
| A19 | temp_water |
°C | Warmwasser |
| A30 | heating_return |
°C | Heizung Rücklauf |
| A31 | heating_set |
°C | Heizung Soll |
| A51 | percent_heat_circ_pump |
% | Heizungsumwälzpumpe |
| A58 | percent_compressor |
% | Verdichterleistung |
| I51 | status_* |
bits | Status-Register (see below) |
| I53 | interruptions |
Unterbrechungen (raw number) | |
| I53 | interruption_flags_evu |
bit | EVU-Sperre (bit 2 of |I53|) |
A-tags are read as raw integers and divided by 10 (Waterkotte's standard fixed-point scaling). I51 is bit-decoded into individual 0/1 fields. I53 is requested once and emitted twice: as the plain number interruptions and bit-decoded as interruption_flags_*.
Status register I51
Bit numbers count from 0 (least significant bit), following openHAB's EcoTouch binding.
| Bit | Value | Field | Description |
| 0 | 1 | status_source_pump |
Quellenpumpe |
| 1 | 2 | status_heating_pump |
Heizungspumpe |
| 2 | 4 | status_evd |
EVD |
| 3 | 8 | status_compressor |
Verdichter 1 |
| 4 | 16 | status_compressor2 |
Verdichter 2 |
| 5 | 32 | status_heater |
Zusatzheizung / Heizstab |
| 6 | 64 | status_alarm |
Alarm / Störung |
| 7 | 128 | status_cooling |
Kühlung |
| 8 | 256 | status_water |
Warmwasser |
| 9 | 512 | status_pool |
Pool |
| 10 | 1024 | status_solar |
Solar |
| 11 | 2048 | status_cooling_4way |
Kühlung 4-Wege-Ventil |
Example: I51 = 355 (256 + 64 + 32 + 2 + 1) → source pump, heating pump, heater, alarm and hot water are on.
Interruptions I53 (EVU)
The pump can report I53 as a negative number. interruption_flags therefore decodes the bits of the absolute value ("abs": true): bit 2 (value 4) is the EVU block (utility lock-out). Example: I53 = -32764 → |I53| = 32764 → interruption_flags_evu = 1; I53 = 0 → 0. Other I53 bits are not documented and are not decoded.
Custom tag list
Set Tag-Preset → Custom (JSON) to define your own tags:
{ "tag": "A1", "name": "outdoor", "scale": 0.1, "unit": "°C" },
{ "tag": "A19", "name": "ww", "scale": 0.1, "unit": "°C" },
{ "tag": "I51", "name": "status", "bits": { "1": "heating_pump", "3": "compressor" } },
{ "tag": "I53", "name": "evu", "abs": true, "bits": { "2": "lock" } }
Field reference:
| Key | Type | Required | Default | Notes |
tag |
string | yes | — | Waterkotte tag (A1, A11, I51, D…, …) |
name |
string | no | same as tag |
key in msg.payload |
scale |
number | no | 1 |
multiplier for the raw integer (0.1 for °C / %) |
unit |
string | no | '' |
not used at runtime, only documentation |
bits |
object | no | — | { "<bit-0-indexed>": "fieldName" }, decodes integer (since 0.1.5 counted from 0) |
abs |
bool | no | false |
decode bits from the absolute value (_raw keeps the sign) |
Options
- Poll (s) — fixed interval polling (
0= read only when an input message arrives) - Bit-Felder flatten — emit
status_alarmrather thanstatus.alarm(default on; nice for InfluxDB schemas) - Rohwerte mitschicken — additionally include
<name>_rawfor every tag
Token & error handling
- Login is performed lazily on the first read.
- The
IDALTokencookie is reused across reads and across allwaterkotte-readnodes that share the same config node. - On
401/403/#Eresponses the token is dropped, the client re-logs-in once and retries the read. - All other failures (network timeout, parse error) propagate as a Node-RED
node.errorand can be caught with acatchnode.
Migrating from a hand-built flow
If your existing flow chains http request → http request → http request … and has a separate String-to-Bitregister subflow, replace the entire chain with one waterkotte-read node. The output object key names line up with the field names commonly used in the community (see preset table above), so InfluxDB writes and downstream switches keep working.
Disclaimer
Not affiliated with Waterkotte GmbH. "Waterkotte" and "EcoTouch" are trademarks of their respective owners. Use at your own risk — this package only reads from the heat pump, never writes.
MIT