node-red-contrib-vallox 0.1.31
Vallox node for serial RS485 protocol.
npm install node-red-contrib-vallox
Vallox nodes for node-red
Platform License NPM Known Vulnerabilities Downloads Total Downloads Package Quality Open Issues Closed Issues ...
This package contains nodes for controlling vallox devices via the serial RS485 API. You must connect the RS485 bus and read the data using e.g. an RS485 to serial converter. Then use a serial node to read the data and feed it to the node.
Requirements
Node-RED 3.1.0 or newer on Node.js 20 or newer. The nodes themselves use only long-standing runtime APIs, so the floor is set by Node.js 20: Node-RED 3.1.0 is the first release that supports it. The test suite runs against that floor.
You also need a byte stream to and from the unit — typically node-red-node-serialport on an RS485 adapter, or an MQTT bridge.
Dependencies
None at runtime — the nodes ship no third-party code and the RS485 protocol is implemented in this package. See Requirements above for the companion node that provides the byte stream.
Disclaimer
This package is not developed nor officially supported by the company Vallox. It is for demonstrating how to communicate to the devices using node-red.
Thanks for your donation
If you want to support this free project. Any help is welcome. You can donate by clicking one of the following links:
Buy Me A Coffee
Credits
Changelog
Changes can be followed here
Getting started
Wire an RS485 transceiver (e.g. an RS485-to-USB adapter) to your Vallox bus and read it with a serial in node, or bridge the stream over MQTT. The serial port settings are 9600 baud, 8 data bits, no parity, 1 stop bit (8N1).
A typical receive-and-send pipeline:
serial in / mqtt in  -->  valloxrx  -->  vallox  -->  valloxtx  -->  serial out / mqtt out
                                       request msg   (only when sending)
  • valloxrx decodes the raw byte stream into structured frames.
  • vallox keeps the latest value of each variable seen for a configured device address (panel or master) and turns request objects into outgoing frames.
  • valloxtx serialises an outgoing frame to the 6-byte buffer that goes on the wire.
Vallox RX Node
Decodes Vallox RS485 telegrams (6-byte frames) from a raw byte stream. Incoming bytes are buffered until a complete frame is available; misaligned leading bytes are dropped at the next start byte (0x01).
  • Input msg.payload — raw bytes from the serial port or MQTT: a Buffer, a Uint8Array, an array of bytes, or the JSON text "[1,17,32,…]" that an MQTT hop makes of an array payload. Anything else is reported on output 2. Chunks need not align with frames, and the shapes may be mixed between messages.
  • Output 1 — decoded frame object with domain, sender, receiver, command, arg, checksum, variable (human name, e.g. FanSpeed), request ("GET" or "SET") and — for SET frames — value (already converted, e.g. fan speed 1-8 or temperature in °C).
  • Output 2 — error string (bad checksum, wrong frame length, …).
See examples/valloxrx.json for a minimal RX-only flow.
Diagnostics — two optional settings, both off by default:
  • Diagnostics — logs every received chunk and every framing decision as hex, and puts running counters in the node status: bytes received, frames decoded out of the number the byte count allows, bytes dropped, checksum failures. A healthy stream is one frame per six bytes with no drops.
  • Capture file — appends every received byte to a file, exactly as it arrived.
Then analyse the capture offline:
node tools/analyse-capture.js C:\temp\vallox.bin
It walks the capture, reports every point where the stream stops being a clean run of 6-byte frames, and says which kind of fault it is: a lost byte (the stream realigns one byte early), an extra byte (realigns one byte late), or a corrupted byte (alignment intact, one frame unreadable). Lost and extra bytes point at the transport — gateway chunking, MQTT queueing; corrupted bytes with the length intact point at the RS485 line itself, such as collisions or missing termination.
Vallox TX Node
Encodes a telegram object into a 6-byte frame, ready for the bus. Normally fed by the vallox node's second output.
  • Input msg.payload — { domain, sender, receiver, command, arg }. The checksum byte is computed and appended automatically.
  • Output 1 — 6-byte array [domain, sender, receiver, command, arg, checksum].
  • Output 2 — error string.
See examples/valloxtx.json for a minimal TX-only flow.
Vallox Node
Holds the in-memory state of one Vallox device (panel or master) and generates outgoing requests.
  • Receiver — RS485 address of the device this node represents:
    • Panel 1-7: 33-39 (0x21-0x27)
    • LON: 40 (0x28)
    • Master 1: 17 (0x11)
    This address is also the sender address of every telegram the node emits, so it must not be one your hardware already uses. See Bus addressing below.
  • Send msg on new data — when checked, output 1 fires every time a matching SET frame updates the state.
  • Write like a panel — a SET produces the three telegrams a real control unit sends (mainboard with the checksum repeated, then all panels, then all mainboards). Unticking sends only the first; the master propagates the change itself.
Inputs (one of three shapes on msg.payload):
  1. A decoded frame from valloxrx (object with a receiver field) — matching frames update the internal state.
  2. A request object { request: "GET" | "SET", variable: "<name>", value: <value> } — produces an outgoing telegram on output 2. A SET on a readonly variable goes to output 3 as an error.
  3. Anything else (or empty payload) — emits the current state snapshot on output 1.
Outputs
  1. Current state object — every variable seen so far, keyed by its human-readable name.
  2. Outgoing telegram object — feed into valloxtx.
  3. Error string — e.g. an attempt to SET a readonly variable.
See examples/vallox.json for a complete RX + state + TX + MQTT flow.
Bus addressing
The protocol assigns each module an address: mainboards 11H-1FH (1-15), panels and remote controls 21H-2FH (1-15). 10H addresses all mainboards at once and 20H all panels. The vallox node's Receiver setting is both the address whose traffic it adopts and the address it sends from — it impersonates a panel.
Do not use an address your own panels occupy
The original Vallox control unit ships as Panel 1 (21H / 33), and each additional panel takes the next address: 22H, 23H, and so on. Those are exactly the values at the top of the Receiver dropdown, so the default choice is usually the wrong one.
Two modules answering to one address is not a configuration error the bus detects. Both consume the master's replies to that address, both may transmit as it, and because a write is broadcast to all panels and all mainboards, a duplicate address propagates confusion rather than containing it.
Pick an address no physical device uses — the far end of the range (27H / 39, Panel 7) is a reasonable default for a single Node-RED instance. To see which addresses are taken, tick Diagnostics on the valloxrx node, capture a minute of traffic and look at the senders:
The capture also tells you what to expect: a two-panel system typically shows panel 1, panel 2 and mainboard 1 talking, and nothing else.
Too many transmitters cause collisions
The bus is a single pair shared by up to 32 modules, and nothing arbitrates access — a module transmits when it has something to say. Two modules starting at once corrupt each other's bytes, and the protocol's only recovery is the requester's own retry: it waits 10 ms for a reply, repeats the request up to ten times, and then puts itself into a fault state. Corrupted frames therefore cost more than the frame; they cost bus time that makes further collisions likelier.
Every panel already polls the master continuously, so the bus is busy before you add anything. In a measured capture the damage rate roughly doubled — one bad frame per 317 bytes against one per 760 — while a panel was writing setpoints, purely because more modules were transmitting.
Practical consequences:
  • Add as few transmitters as you can. One Node-RED node per system, not one per dashboard.
  • Poll sparingly. One GET every few seconds covers a rotation of registers; the panels' own polling fills in the rest. A tight loop of GETs is the easiest way to make a quiet bus noisy.
  • Prefer the broadcasts where they exist. Humidity, both CO2 bytes and the four temperatures arrive every 12 seconds unasked — polling them adds traffic for nothing.
  • Expect occasional checksum errors and let the retry work. A frame lost to a collision reappears on the next poll; treat a persistent rate as a wiring problem (termination, biasing, stub length), not something to fix by polling harder.
Example: setting the fan speed
To change the fan speed, send a request object to the vallox node and wire its output 2 into a valloxtx node. The function node that builds the request:
msg.payload = {
    request: 'SET',
    variable: 'FanSpeed',
    value: msg.payload, // 1 .. 8
The same shape is used for every writable variable — see the Command reference below for the full list. Temperature setpoints (HeatingSetPoint, PreHeatingSetPoint, InputFanStop, HRCBypass) take a value in °C; the package converts to the NTC sensor byte automatically.
Reading the current state is even simpler: send any non-empty message (or an empty inject) to the vallox node and it emits the latest cached state on output 1.
The full flow with fan-speed injection buttons, an HTTP state endpoint and an MQTT bridge is in examples/vallox.json.
Example flows
Import these from the Node-RED editor menu (Import → Examples → node-red-contrib-vallox).
Flow What it shows
vallox-commands.json One inject per writable variable — every command this package can send, with realistic values
vallox-monitor.json Decoding the bus and caching every variable, with replayable sample frames and a corrupt one
vallox.json Complete RX + state + TX flow with an MQTT bridge
valloxrx.json Minimal receive-only flow
valloxtx.json Minimal send-only flow
serialmqtt.json Bridging the serial port to MQTT, for running the decoder on another host
The two generated flows need no hardware: their inject nodes replay real frames and real requests, and test/examples.test.js checks that every value in them is one the package can actually encode.
Command reference
Two request shapes go to the vallox node. GET asks the unit for a register, SET writes one:
msg.payload = { request: 'GET', variable: 'TemperatureInside' };
msg.payload = { request: 'SET', variable: 'FanSpeed', value: 4 };
Either way the node emits the resulting telegram on output 2; wire that into valloxtx. The answer to a GET arrives like any other bus traffic — through valloxrx, into the node's cache. A SET aimed at a read-only variable goes to output 3 instead, and no telegram is produced.
Command bytes and the writable/read-only split are the protocol's own, cross-checked against doc/vallox-rs485-protocol.md and doc/protocol.txt by the test suite.
Writable variables
Variable Command Value Meaning
BasicHumidityLevel 0xae %RH Basic humidity level (AEH), the threshold for humidity-driven boosting.
CellDefrostingHysteresis 0xb2 °C Anti-freeze hysteresis (B2H), byte = °C × 3.
CO2SetPointLower 0xb4 ppm, low byte Lower byte of the 16-bit CO2 setpoint (B4H).
CO2SetPointUpper 0xb3 ppm, high byte Upper byte of the 16-bit CO2 setpoint (B3H).
DCFanInputAdjustment 0xb0 % DC supply air fan control setpoint (B0H).
DCFanOutputAdjustment 0xb1 % DC exhaust fan control setpoint (B1H).
FanSpeed 0x29 1 - 8 Current fan speed (29H). Encoded on the wire as 01H,03H,07H,0FH,1FH,3FH,7FH,FFH.
FanSpeedMax 0xa5 1 - 8 Highest speed the unit may select while adjusting (A5H).
FanSpeedMin 0xa9 1 - 8 Basic fan speed (A9H). The doc calls this "basic", not "minimum".
Flags6 0x71 object or byte 71H. Set FirePlaceSwitchActivator (bit 5) to start the fireplace/booster; bits 4 and 6 are read-only.
HeatingSetPoint 0xa4 °C Post-heating setpoint (A4H), NTC scale.
HRCBypass 0xaf °C Heat-recovery cell bypass temperature (AFH), NTC scale.
InputFanStop 0xa8 °C Supply air fan stops below this temperature (A8H), NTC scale.
MaintenanceMonthCounter 0xab months Months remaining until the next service alarm (ABH), counts down.
PostHeatingOffTime 0x56 % Post-heating off-time counter (56H), byte = % × 2.5.
PostHeatingOnCounter 0x55 % Post-heating on-time counter (55H), byte = % × 2.5.
PreHeatingSetPoint 0xa7 °C Pre-heating switching temperature (A7H), NTC scale.
Program 0xaa object or byte Adjustment interval and mode bits (AAH). Write back a decoded object or a raw byte.
Program2 0xb5 object or byte Max speed limit mode (B5H). Write back a decoded object or a raw byte.
Resume 0x8f 0 Allow modules to transmit (8FH). Write-only; DATA is always 0.
Select 0xa3 object or byte Panel keys and indicator lamps (A3H). Bits 0-3 (power, CO2, %RH, post-heating) are writable; 4-7 are read-only lamps.
ServiceReminder 0xa6 months Service reminder interval (A6H).
Suspend 0x91 0 Prohibit modules from transmitting (91H). Write-only; DATA is always 0.
Read-only variables
CO2High 0x2b ppm, high byte Upper byte of the measured 16-bit CO2 concentration (2BH).
CO2Low 0x2c ppm, low byte Lower byte of the measured 16-bit CO2 concentration (2CH).
CurrentIncoming 0x2e raw 0 - 255 Current/voltage message to the machine (2EH).
FirePlaceBoosterCounter 0x79 minutes Remaining minutes of the fireplace/booster function (79H), counts down. Start the function via Flags6 bit 5.
Flags1 0x6c object 6CH. Not described in the protocol doc; decoded as Bit0 - Bit7.
Flags2 0x6d object Speed requests and alarms (6DH), incl. CO2Alarm, FrostAlarm.
Flags3 0x6e object 6EH. Not described in the protocol doc; decoded as Bit0 - Bit7.
Flags4 0x6f object 6FH: FrostAlarmWaterRadiator, SlaveMasterSelection.
Flags5 0x70 object 70H: PreHeatingStatus.
Humidity 0x2a %RH Highest measured relative humidity of the two sensors (2AH).
HumiditySensor1 0x2f %RH Relative humidity measured by sensor 1 (2FH).
HumiditySensor2 0x30 %RH Relative humidity measured by sensor 2 (30H).
InstalledCO2Sensors 0x2d object Which CO2 sensors are fitted (2DH), Sensor1Installed - 5.
IoPortFanSpeedRelays 0x06 object Fan speed relay states (06H), FanSpeedRelay1 - 8.
IoPortMultiPurpose1 0x07 object I/O port 1 (07H); only PostHeatingOn (bit 5) is defined.
IoPortMultiPurpose2 0x08 object I/O port 2 (08H): damper, fault relay, fans, pre-heating, fireplace booster.
LastErrorNumber 0x36 text Last fault, decoded to a sentence (36H); unknown codes come through as 0x...
PostHeatingTargetValue 0x57 °C Target temperature of the air blown into the zone (57H), NTC scale.
TemperatureExhaust 0x33 °C Exhaust air temperature (33H), NTC scale.
TemperatureIncoming 0x35 °C Supply air temperature (35H), NTC scale.
TemperatureInside 0x34 °C Extract air temperature (34H), NTC scale.
TemperatureOutside 0x32 °C Outdoor temperature (32H), NTC scale.
Decoded bit fields
Variables whose value is an object decode to the fields below. Entries named BitN are positions the protocol document leaves undefined; they are still reported, which is what lets a decoded object be written straight back without losing the bits the unit had set.
Variable Fields (bit 0 → 7)
IoPortFanSpeedRelays FanSpeedRelay1, FanSpeedRelay2, FanSpeedRelay3, FanSpeedRelay4, FanSpeedRelay5, FanSpeedRelay6, FanSpeedRelay7, FanSpeedRelay8
IoPortMultiPurpose1 Bit0, Bit1, Bit2, Bit3, Bit4, PostHeatingOn, Bit6, Bit7
IoPortMultiPurpose2 Bit0, DamperMotorPosition, FaultSignalRelayClosed, SupplyFanOff, PreHeatingOn, ExhaustFanOff, FireplaceBoosterClosed, Bit7
InstalledCO2Sensors Bit0, Sensor1Installed, Sensor2Installed, Sensor3Installed, Sensor4Installed, Sensor5Installed, Bit6, Bit7
Flags1 Bit0, Bit1, Bit2, Bit3, Bit4, Bit5, Bit6, Bit7
Flags2 CO2HigherSpeedRequest, CO2LowerSpeedRequest, HumiditySpeedRequest, SwitchSpeedRequest, Bit4, Bit5, CO2Alarm, FrostAlarm
Flags3 Bit0, Bit1, Bit2, Bit3, Bit4, Bit5, Bit6, Bit7
Flags4 Bit0, Bit1, Bit2, Bit3, FrostAlarmWaterRadiator, Bit5, Bit6, SlaveMasterSelection
Flags5 Bit0, Bit1, Bit2, Bit3, Bit4, Bit5, Bit6, PreHeatingStatus
Flags6 Bit0, Bit1, Bit2, Bit3, RemoteMonitoringControl, FirePlaceSwitchActivator, FirePlaceBoosterStatus, Bit7
Select PowerState, Co2AdjustState, HumidityAdjustState, HeatingState, FilterGuardIndicator, HeatingIndicator, FaultIndicator, ServiceReminderIndicator
Program AdjustmentIntervalMinutes, AutomaticHumidityLevelSeekerState, BoostSwitchMode, RadiatorType, CascadeAdjust
Program2 MaxSpeedLimitMode, Bit1, Bit2, Bit3, Bit4, Bit5, Bit6, Bit7
Monitoring all variables
The master broadcasts seven registers to all panels every 12 seconds — Humidity, CO2High, CO2Low and the four temperatures. Everything else has to be asked for. Wire the bus through valloxrx into a vallox node and both paths land in the same cache:
serial in  →  valloxrx  →  vallox  →  debug
                        GET requests  →  valloxtx  →  serial out
A practical setup polls the registers you care about on a rotation — one every few seconds is plenty, and the panels do the same thing:
// in a function node driven by an inject on a repeat
const registers = ['FanSpeed', 'Select', 'FanSpeedMax', 'HeatingSetPoint', 'LastErrorNumber'];
const i = (context.get('i') || 0) % registers.length;
context.set('i', i + 1);
msg.payload = { request: 'GET', variable: registers[i] };
Two ways to read the cache:
  • Push — tick Send msg on new data and output 1 fires on every state change.
  • Pull — send the node any message with an empty payload; the current snapshot arrives on output 1.
The snapshot is a flat object keyed by the variable names in the tables, plus Receiver. Variables that have not been seen yet are simply absent, so guard with a check rather than assuming a key exists. A vallox node only accepts frames addressed to its configured receiver or to that address's group (high nibble), so a panel node at 0x21 also sees frames sent to 0x20.
See examples/vallox-monitor.json for a ready-made flow.
Changing a bit field
Select, Flags6, Program and Program2 are single bytes holding several settings, and only some bits may be written. Read the current value, change what you want and write the whole object back — the decode/encode pair round-trips exactly, so the bits you did not touch are returned unchanged:
// switch the unit on: Select bit 0
const select = { ...flow.get('valloxState').Select, PowerState: true };
msg.payload = { request: 'SET', variable: 'Select', value: select };
// start the fireplace/booster function: Flags6 bit 5
const flags = { ...flow.get('valloxState').Flags6, FirePlaceSwitchActivator: true };
msg.payload = { request: 'SET', variable: 'Flags6', value: flags };
A raw byte works too — value: 0x0d is equivalent to the object form.
Notes and known deviations
  • Suspend and Resume stop and start bus traffic for every module. They exist because the unit uses them around CO2 sensor interaction; sending them yourself is rarely what you want. The vallox node watches for them and refuses to emit telegrams while transmission is prohibited, reporting the refusal on output 3. Because a missed 8FH would otherwise wedge the node, that block also lapses by itself after 10 seconds.
  • FanSpeedMin is the protocol's "basic fan speed" (A9H), not a floor. The name is kept for compatibility with existing flows.
  • Flags1 (0x6C) and Flags3 (0x6E) are not in the protocol document. They decode to bare Bit0-Bit7.
  • IoPortMultiPurpose2 (0x08) is treated as read-only although the document leaves bits 3 and 5 unmarked. Those bits stop the supply and exhaust fans, and 0x06 carries an explicit warning that driving the I/O ports can damage the transformer. Use FanSpeed instead.
  • Program2 bits 1-7 are undefined in the document. They are decoded and written back as-is.
  • The misspelled names PostHeastingOnCounter and InstalledC02Sensors are still accepted as input for backwards compatibility. Decoded messages always use the corrected spelling.
  • A write is three telegrams, matching what a real control unit sends: to the mainboard with the checksum repeated (7 bytes), then to all panels (0x20), then to all mainboards (0x10). This was taken from a capture of an original panel changing the fan speed, and the encoded bytes are identical to it. Untick Write like a panel to send only the telegram to the mainboard; the master propagates the change itself, so that is usually enough.
  • The configured receiver is also the sender address of outgoing telegrams. Choose an address no physical panel occupies, or two devices will answer to the same address.
  • CellDefrostingHysteresis follows the document (03H ≈ 1 °C, so byte = °C × 3). Note that the valloxserial Arduino library treats B2H as an NTC temperature instead; the two disagree.
Author: Karl-Heinz Wind
The MIT License (MIT) Copyright (c) 2023 by Karl-Heinz Wind
THE SOFTWARE IS PROVIDED "AS IS", WITHOUT WARRANTY OF ANY KIND, EXPRESS OR IMPLIED, INCLUDING BUT NOT LIMITED TO THE WARRANTIES OF MERCHANTABILITY, FITNESS FOR A PARTICULAR PURPOSE AND NON-INFRINGEMENT. IN NO EVENT SHALL THE AUTHORS OR COPYRIGHT HOLDERS BE LIABLE FOR ANY CLAIM, DAMAGES OR OTHER LIABILITY, WHETHER IN AN ACTION OF CONTRACT, TORT OR OTHERWISE, ARISING FROM, OUT OF OR IN CONNECTION WITH THE SOFTWARE OR THE USE OR OTHER DEALINGS IN THE SOFTWARE.
Version: 0.1.31
Updated 3 months, 3 weeks ago
Rating: 5.0 2
3 in the last week
  • valloxrx
  • valloxtx
  • vallox
  • vallox