node-red-contrib-s7-suite 0.0.10
Node-RED nodes for Siemens S7 PLC communication with dual backend support (nodes7 + node-snap7)
Node-RED nodes for Siemens S7 PLC communication with dual backend support.
Overview
s7-suite is a TypeScript-based Node-RED package for communicating with Siemens S7 PLCs. It supports multiple communication backends and is designed for both production deployments and hardware-free development.
Highlights
Multiple backends — Pick the backend that fits your environment per connection:
nodes7— pure JavaScript, no native compilation requirednode-snap7— native Snap7 library, enables advanced features like block listing, SZL reads, and CPU controlsim— built-in simulator generating dynamic values (sine waves, counters, sawtooth signals) for development without a physical PLC
Flexible address formats — Write addresses in the style you prefer: nodes7-style (DB1,REAL0), IEC-style (DB1.DBD0), or area-style (MW4, I0.1, QD8). The address parser handles conversion transparently. See Addresses and data types.
Smart polling — The trigger node supports edge detection (rising, falling, any) for booleans and configurable deadband for numeric values, reducing unnecessary messages in flows.
PLC browsing — Discover data blocks directly from Node-RED. With snap7 this uses native block listing; with nodes7 a probe-based approach with rate limiting explores the PLC address space safely.
Robust connections — Connection manager with request queuing (max 100), automatic reconnection with exponential backoff, a link check while idle so the node status follows the PLC, and structured error codes (S7Error with error code and cause chain).
Flexible read/write modes — Single values, combined objects, raw buffers, structured schemas, or unpacked bit arrays.
Bulk tag import — Import full PLC tag lists into the read node with one click. Supported files: a TIA Portal tag table Export (.xlsx, .xml or .sdf), SimaticML XML from TIA Portal Openness (.xml), Step 7 symbol exports (.csv/.tsv), and STEP 7 V5 hardware configuration exports (.cfg). For CSV and Excel it auto-detects column names (name/symbol/tag and address) and separators (tab/semicolon/comma). Imported tags get human-readable labels used as object keys in the output.
Offline CFG import — Upload a STEP 7 .cfg file to discover tags and pick addresses without a live PLC connection. Useful for engineering offline, reviewing code, or demoing flows. The browse dialog can switch between live and cfg source on the fly.
- s7-config — Connection configuration with backend selection and auto-reconnect. Host, port, rack, slot, TSAPs and timeouts can each come from an environment variable, so one flow can run against different PLCs
- s7-read — Read PLC data in multiple output modes: single value, combined object, raw buffer, struct, or bit array
- s7-write — Write single values, arrays, strings or whole structs to PLC memory areas, with dynamic address via
msg.topic - s7-trigger — Polling with edge detection and deadband filtering
- s7-browse — Discover PLC data blocks with category filtering and search; supports both live PLC and offline
.cfgimport - s7-control — CPU control actions: Start, Stop, Cold Start (snap7 backend only)
Supported PLCs
S7-200, S7-300, S7-400, S7-1200, S7-1500, LOGO!
Backends
| Backend | Package | Description |
| nodes7 | nodes7 |
Pure JavaScript, no native compilation needed |
| snap7 | node-snap7 |
Native library via Snap7, optional |
| sim | built-in | Simulation backend for development and testing |
Three address styles are accepted and can be mixed freely:
| Style | Examples |
| nodes7 | DB1,REAL0 · DB1,X0.3 · DB1,INT20.3 · DB1,STRING50.20 |
| IEC | DB1.DBX0.3 · DB1.DBB4 · DB1.DBW6 · DB1.DBD8 |
| Area | M0.1 · MB4 · MW6 · MD8 · I0.0 · IB0 · QW2 · C1 · T2 |
What the numbers after the offset mean depends on the type:
| Address | Meaning |
DB1,X10.3 · M10.3 |
bit 3 of byte 10 (BOOL can be written instead of X) |
DB1,X10.3.8 · M10.3.8 |
8 consecutive bits starting at bit 3 of byte 10 — an Array[0..7] of Bool |
DB1,INT20.3 · MB20.3 |
array of 3 values. The longer form DB1,INT20.0.3 means the same |
DB1,STRING50.20 |
a STRING[20] at offset 50. The length can be left off when writing a string that is already declared in the PLC |
An address with a length reads as an array and is written from an array of exactly that many values; a byte array also accepts a Buffer.
| Type | Size | Value in Node-RED | nodes7 backend |
BOOL / X |
1 bit | boolean | ✓ |
BYTE, CHAR |
1 byte | number, 1-character string | ✓ |
WORD, INT |
2 bytes | number | ✓ |
DWORD, DINT |
4 bytes | number | ✓ |
REAL, LREAL |
4 / 8 bytes | number | ✓ |
STRING |
length + 2 bytes | string | ✓ (reads need the length in the address) |
DT, DTZ |
8 bytes | Date — a PLC DATE_AND_TIME, as server-local time (DT) or UTC (DTZ) |
DTL, DTLZ |
12 bytes | Date — a PLC DTL, as server-local time (DTL) or UTC (DTLZ) |
USINT, UINT, UDINT |
1 / 2 / 4 bytes | number | snap7 only |
LINT, ULINT |
8 bytes | number, BigInt or string (see below) | snap7 only |
WSTRING |
2 × length + 4 bytes | string | writes only; reads need snap7 |
DATE |
2 bytes | string YYYY-MM-DD |
snap7 only |
TIME, TIME_OF_DAY |
4 bytes | number (ms) | snap7 only |
S5TIME |
2 bytes | number (ms) | snap7 only |
DATE_AND_TIME |
8 bytes | ISO string (UTC) | snap7 only |
The sim backend supports every type. Counters and timers (C1, T2) also need the snap7 backend. On the nodes7 backend an unsupported type is reported as an error that names the address, never as a silent null.
Dates — Writes to DT, DTZ, DTL and DTLZ accept a Date, an ISO string or milliseconds since 1970. A PLC date has no time zone: use the Z form when the PLC keeps UTC, the plain form when it keeps local time.
64-bit integers — A JavaScript number is exact only up to 2^53. The LINT/ULINT as setting on s7-config chooses how LINT and ULINT are returned: Number (default), BigInt (exact, but cannot pass through JSON.stringify, so not through MQTT or HTTP) or String (exact and safe to send anywhere). Writes accept all three.
Strings — A write changes only the string's current length and characters, never its declared max length or anything after it. A value longer than the string is rejected.
Environment variables
Host, port, rack, slot, the TSAPs, the timeouts and the reconnect intervals on s7-config each take either a value or the name of an environment variable (pick env in the field's type menu). Node-RED's flow and global environment variables work as well as the process environment, so the same flow can be deployed against different PLCs. A variable that is unset, or not a number where one is needed, is reported as a config error and the node does not connect — it never falls back to a default.
s7-trigger's Interval and Deadband work the same way. An unset or unusable variable stops that trigger with an error.
Connection control
Two settings on s7-config let a flow manage the connection, following the pattern of Node-RED's MQTT nodes:
| Setting | Default | Description |
| Auto connect | on | Connect on deploy and retry after a failure or a lost link. Off, the connection stays down until a flow sends msg.action = "connect", and a failure or lost link is not retried |
| Dynamic control | off | s7-read, s7-write, s7-control and s7-browse accept msg.action. Off, msg.action is ignored, so existing flows are unaffected |
A message carrying msg.action acts on the connection and does no PLC I/O:
msg.action |
Effect |
connect |
Connects. Already connected is a success; a pending retry is brought forward |
disconnect |
Disconnects and stops retrying until told to connect |
reconnect |
Disconnects, then connects with the retry backoff reset |
status |
Sends the message on with msg.payload set to the connection report (below) and msg.s7 to { op: "status", server, timestamp, durationMs } |
"id": "a1b2c3d4", "name": "Line 1 PLC",
"state": "connected", "since": 1791100000000,
"lastError": "Connection lost", "lastErrorAt": 1791099990000,
"backend": "snap7", "host": "192.168.0.10", "port": 102, "rack": 0, "slot": 1, "plcType": "S7-1500",
"autoConnect": true, "allowDynamic": true, "configError": null
state is connected, connecting, reconnecting, error or disconnected, and since is when it entered that state. lastError is the most recent connect failure or lost link, kept after the connection recovers. The action affects the connection, so every node using that s7-config sees the result. A failed connect or reconnect, or an unknown action, is reported as the node's error, so a Catch node can handle it. connect, disconnect and reconnect send nothing on: to carry on once one has finished, use a Complete node. Wire a status reply to a debug or switch node rather than straight into another S7 node, which would treat it as an ordinary message to read or write with.
Output details (msg.s7)
Every S7 node adds msg.s7 to the messages it sends, with the same shape on each, so a switch, log or database node can use it whatever S7 node the message came from:
"op": "read",
"server": "Line 1 PLC",
"source": "flow.plc.addresses",
"addresses": { "speed": "DB1,INT0", "temp": "DB1,REAL4" },
"timestamp": 1791100000000,
"durationMs": 12
| Property | Description |
op |
read, write, trigger, control or browse, or status on the reply to msg.action status |
server |
The s7-config's name, or host:port when it has none. Left out when s7-browse reads a .cfg file |
source |
Where the address came from: config (set in the node), msg.payload (s7-write multi-write), or the property, such as flow.plc.addresses or env.PLC_ADDRESS |
address |
The address, when one was read or written (the base address for struct mode) |
addresses |
When msg.payload is keyed by label or address (s7-read object output or several addresses, s7-write multi-write), the same keys, each with its address |
timestamp |
When the message was sent, in ms since 1970 |
durationMs |
From the message arriving to it being sent. For s7-trigger, from the start of the poll that saw the change |
A property that doesn't apply is left out. Any msg.s7 on the input message is replaced. s7-control, s7-browse and the status reply have only op, server, timestamp and durationMs.
Node API
s7-read
Any message triggers a read. The node reads the addresses and schema set in it; nothing in the message changes them. To take them from the message, set Address src or Schema to msg (or flow, global, env) and name the property:
| Setting | Type | Description |
| Address src | msg / flow / global / env |
An address string (space- or semicolon-separated), an array of addresses, or { label: address }, whose labels become the output keys |
| Schema | msg / flow / global |
The struct schema, as an array or a JSON string (struct mode only) |
msg.payload |
any | Output: read value(s) |
msg.s7 |
object | Output: what was read, where the address came from, and timing (Output details) |
Output modes:
- single —
msg.payload= single value (or object if multiple addresses) - object —
msg.payload={ "DB1,REAL0": 23.5, "DB1,INT4": 100 } - buffer —
msg.payload= rawBufferof the requested memory area - struct —
msg.payload={ fieldName: value, ... }based on schema definition - bits —
msg.payload=boolean[]with each bit unpacked (LSB first per byte)
In the editor, Add address starts a new row from the one above it, keeping the type and notation: DB1,REAL0 is followed by DB1,REAL4, DB1.DBD0 by DB1.DBD4, MW10 by MW12 and I0.7 by I1.0. Arrays and strings move past their whole length, and a label ending in a number counts on (Temp1, Temp2). The guess is selected, so typing replaces it. The struct schema lists in s7-read and s7-write do the same for Add field: the new field has the previous field's type, and its length for a string, at the next free offset (STRING at 2 with length 10 is followed by a STRING at 14 with length 10), or the next bit for a BOOL. Only the name is left to type.
If some addresses in a read fail, the rest are still sent and the failed ones are null, with a warning naming them. If they all fail, the node reports an error. Both backends behave the same way.
s7-write
The node writes to the address and with the schema set in it; nothing else in the message changes them. To take them from the message, set the address type or Schema to msg (or flow, global, env) and name the property:
| Setting / property | Type | Description |
| Address | str / msg / flow / global / env |
One address string (single and struct modes), for example msg.topic |
msg.payload |
any | Value to write (type must match address data type). For an address with a length (DB1,INT20.3), an array of that many values, or a Buffer for a byte array |
On success, the input message is passed through to the output, with msg.s7 saying what was written (Output details).
s7-trigger
The node has no input: it starts polling once the PLC is connected, and is configured in the editor.
| Interval | num / env |
Polling interval in ms, a whole number of 1 or more (default 1000) |
| Edge mode | select | any, rising or falling. Rising and falling apply to booleans and fire on every false to true (or true to false); their first poll of a boolean sends nothing. any sends the first value read |
| Deadband | num / env |
Smallest change in a numeric value, from the value last sent, that triggers a message, 0 or more (default 0) |
msg.payload |
any | Output: new value |
msg.topic |
string | Output: address that changed |
msg.oldValue |
any | Output: previous value |
msg.s7 |
object | Output: the address that changed and timing (Output details) |
s7-browse
Send any message to trigger. Output msg.payload contains { blocks, areas, addresses, cpuInfo? }. Output msg.s7 is { op: "browse", server, timestamp, durationMs } (Output details).
s7-control
| Property | Type | Description |
msg.payload |
string | Input: action override (start, stop, coldstart, reset) |
msg.payload |
object | Output: { action, success: true } |
msg.s7 |
object | Output: { op: "control", server, timestamp, durationMs } (Output details) |
Requires the snap7 backend. Send a message to execute the configured action, or override via msg.payload.
Troubleshooting
node-snap7 not installed — The snap7 backend requires the native node-snap7 package. Install it with npm install node-snap7. If compilation fails, ensure build tools are installed (build-essential on Debian/Ubuntu, Xcode CLI tools on macOS).
Connection timeout — Verify the PLC IP is reachable (ping <ip>). Check that rack/slot values match your hardware. For S7-1200/1500, ensure "Permit access with PUT/GET" is enabled in the PLC settings.
LOGO connection — LOGO PLCs require TSAP-based connections. Set PLC Type to "LOGO" and configure Local TSAP (e.g. 0x0100) and Remote TSAP (e.g. 0x0200). TSAPs are hex: 0x0100, 0100 and 01.00 (as LOGO! Soft Comfort shows them) all mean the same, and a decimal number is read as hex too.
Address parse errors — Verify address format. Examples: DB1,REAL0, DB1.DBD0, MW4, I0.1, QB0. See Addresses and data types.
"isn't supported by the nodes7 backend" — nodes7 has no support for that data type (see the table in Addresses and data types). Switch the connection's backend to snap7.
"bad quality for …" — The PLC rejected the address: the DB does not exist, or the address runs past the end of the DB or area.
Excel import does nothing — XLSX parsing requires the SheetJS library, which is loaded on demand from a public CDN. If your Node-RED editor runs in an air-gapped environment, export your tag list as .csv from Excel/TIA Portal instead.
Remote I/O via Profibus/Profinet not browsable — The browse node scans local rack I/O (areas I/Q, M, DB, C, T) and PLC blocks. Distributed I/O addresses on remote stations (Profibus DP couplers, Profinet IO) are reachable for read/write using the standard IB/IW/ID/QB/QW/QD syntax with the absolute peripheral address, but they will not appear in the browse results since they are not enumerable through the standard S7 protocol.
Offline browsing without a PLC — Switch the browse dialog source from live to cfg and upload a STEP 7 .cfg export of your hardware configuration. Tags from the cfg are then available in the address picker just like live blocks. Sample file: test-assets/prod.cfg.
Test Assets
The test-assets/ folder in the repo contains shared test material for contributors and bug reproductions:
tag-lists/— sample CSV/Excel tag exports for the bulk-import featureflows/— reproducible Node-RED flows that exercise specific scenariosplc-programs/— STEP 7 / TIA Portal source code that produced the test datacaptures/— Wireshark.pcaps with the S7Comm dissectordocs/— datasheets, screenshots, vendor manuals
This folder is not shipped with the npm package or Docker image. See test-assets/README.md for conventions when contributing files.
Node-RED Palette
Search for node-red-contrib-s7-suite in the Node-RED palette manager.
npm
npm install node-red-contrib-s7-suite
Docker
docker compose up -d
Node-RED is then available at http://localhost:1885 with the S7 nodes pre-installed.
Development Setup
Prerequisites
- Node.js >= 18
- npm
Getting Started
git clone https://github.com/blanpa/node-red-contrib-s7-suite.git
cd node-red-contrib-s7-suite
npm install
npm run build
Scripts
| Command | Description |
npm run build |
Compile TypeScript and copy HTML/icons to dist/ |
npm test |
Run tests with coverage (threshold: 80%) |
npm run lint |
Run ESLint |
npm run lint:fix |
Run ESLint with auto-fix |
npm run format |
Format code with Prettier |
Project Structure
src/
├── backend/ # PLC communication backends (nodes7, snap7, sim)
├── core/ # Address parser, connection manager, poller, rate limiter
├── nodes/ # Node-RED node definitions (HTML + TypeScript)
│ ├── s7-config/
│ ├── s7-read/
│ ├── s7-write/
│ ├── s7-trigger/
│ ├── s7-browse/
│ ├── s7-control/
│ └── shared/ # Shared helpers (status updater)
├── types/ # TypeScript type definitions
├── utils/ # Error codes and helpers
└── icons/ # Node icons
test/
├── helpers/ # Test utilities and mocks
└── unit/ # Unit tests (backend + core)
Contributing
Contributions are welcome! Please follow these steps:
1. Fork & Branch
git checkout -b feature/my-feature
Use a descriptive branch name with a prefix:
feature/for new featuresfix/for bug fixesdocs/for documentation changesrefactor/for code refactoring
2. Code Style
This project uses ESLint and Prettier. Make sure your code passes linting before committing:
npm run lint
npm run format
3. Tests
All new features and bug fixes must include tests. The project enforces a minimum coverage threshold of 80% on branches, functions, lines, and statements.
npm test
4. Commit Messages
Use clear, concise commit messages:
feat: add support for S7-1500 optimized blocks
fix: handle connection timeout on slow networks
docs: add Docker deployment instructions
5. Pull Request
- Make sure all tests pass and linting is clean
- Provide a clear description of what your PR does and why
- Reference any related issues
Development Tips
- Use the sim backend for development — no physical PLC required
- Import
examples/test-flows.jsoninto Node-RED for a ready-made test setup - Run the project in Docker for a quick local environment:
Thanks to everyone who has contributed code, bug reports and test material:
| Contributor | Contributions | |
| @blanpa | Author and maintainer | |
| @Steve-Mcl | Editor fixes and layout, environment variables for connection settings, DT/DTL and exact 64-bit types, string writes, connection-loss detection, error messages, TIA Portal .xml/.sdf import, and many backend fixes (0.0.9) |
| @birosz | Test material and bug reports |
Bug reports that led to fixes: @BurgerMirco, @robbin2109.
Want to be on this list? See Contributing.
Changelog
See CHANGELOG.md for release notes.
Sponsor this project
This package is developed and maintained in my own time. If it saves you some, consider supporting it:
Apache License 2.0 — see LICENSE and NOTICE.
Copyright 2026 blanpa
Contributing and forks
Pull requests are welcome, including large ones. If you are planning a bigger change — a dependency migration, a restructure, new nodes — please open an issue first. We are happy to discuss it and to land substantial work here; that is usually less effort than maintaining a parallel package, and it keeps a single place for users to report bugs.
If you do publish a fork under its own package name, please also rename the
Node-RED node type IDs (for example myprefix-s7-suite-*) and use your own palette
category. Node-RED refuses to register a node type that is already claimed, so
identical type IDs make it impossible to install both packages side by side.