node-red-contrib-pid-controller-isa 0.3.2
Industrial-grade PID controller using ISA standard algorithm for Node-RED
npm install node-red-contrib-pid-controller-isa
Industrial-grade PID controller for Node-RED using the ISA standard algorithm. Comparable to Siemens FB41, Beckhoff Tc2_Pid, and Allen-Bradley PIDE.
  • ISA Standard PID Algorithm - Industry-standard formulation
  • Feed-Forward - Disturbance compensation with safety limiting
  • Tracking Mode - Cascade control with NaN-safe fallback
  • Anti-Windup - Conditional integration prevents saturation
  • Integrator Soft Clamp - Fast recovery after long saturation
  • Bumpless Transfer - Smooth transition from manual to auto mode
  • Derivative Smoothing - EMA filter, numerically stable for any dt
  • Output Rate Limiting - Protects actuators from rapid changes
  • Max Interval Timeout - Detects sensor failures
  • NaN/Infinity Protection - Robust operation with back-calculation recovery
  • Reverse Acting Mode - For cooling control applications
  • Centered Band Mode - DDC-style 50% output at setpoint
  • Xp Mode - Proportional band (physically correct: Kp = outputSpan/Xp)
  • Industry-Compatible Aliases - pv, sp, ff, external, cascade
  • Full Runtime Override - All parameters adjustable via messages
Or install via the Node-RED palette manager.
Formula (ISA Standard)
output = Kp × [ e(t) + (1/Ti) × ∫e(t)dt + Td × de(t)/dt ] + FF
Direct:  e(t) = setpoint - processValue
Reverse: e(t) = processValue - setpoint
FF = ffGain × feedForward
Parameter Description Default
Setpoint Target value 20
Use Xp Use proportional band instead of Kp false
Kp / Xp Proportional gain or band % (Kp = outputSpan/Xp) 1.0
Ti Integral time in seconds (0 = disabled) 60
Td Derivative time in seconds (0 = disabled) 0
Output Min Minimum output % 0
Output Max Maximum output % 100
Rate Limit Max change per second, %/s (0 = disabled) 0
Max Interval Max time between samples (0 = disabled) 0
Reverse Acting Enable for cooling control false
Centered Band 50% output at setpoint (DDC-style) false
Enable Feed-Forward Enable msg.feedForward input false
FF Gain Feed-forward scaling factor 1.0
Manual Mode Start in manual mode false
Manual Value Initial manual output % 0
Decimals Output decimal places 1
Inputs
Property Type Description
payload / pv number Required. Process value (temperature, pressure, etc.)
setpoint / sp number Override setpoint (sticky - stays until changed or reset)
Kp number Override proportional gain
Xp number Override proportional band (converted to Kp = outputSpan/Xp)
Ti number Override integral time (seconds)
Td number Override derivative time (seconds)
feedForward / ff number Feed-forward value (limited to ±outputSpan)
trackingValue / external / cascade number Tracking value for cascade control
manual boolean Switch to manual (true) or auto (false)
manualValue number Set manual output value (0-100%)
reset boolean Reset controller state and restore default setpoint
Outputs
Output 1 - Control Output
payload number Control output (0-100%)
pid object Detailed PID information
The pid object contains:
  processValue: 18,      // Current process value
  setpoint: 22,          // Active setpoint
  error: 4,              // Current error
  output: 45.2,          // Control output
  P: 4,                  // Proportional term
  I: 1.2,                // Integral term
  D: 0,                  // Derivative term
  FF: 0,                 // Feed-forward term
  Kp: 1,                 // Active Kp
  Ti: 60,                // Active Ti
  Td: 0,                 // Active Td
  dt: 1.003,             // Time since last calculation (s)
  clamped: false,        // Output was clamped
  clampedAt: null,       // "min" or "max" if clamped
  antiWindup: false,     // Anti-windup was active
  manual: false,         // Manual mode active
  reverseActing: false,  // Reverse acting mode
  centeredBand: false,   // Centered band mode
  rateLimit: 0,          // Rate limit setting
  rateLimited: false,    // Output was rate limited
  maxInterval: 0,        // Max interval setting
  intervalExceeded: false, // Interval was exceeded
  ffEnable: false,       // Feed-forward enabled
  ffGain: 1.0,           // Feed-forward gain
  tracking: undefined,   // Tracking value if provided
  trackingActive: false  // Tracking mode was active
Output 2 - Status
payload.manual boolean Manual mode active
payload.setpoint number Active setpoint
payload.processValue number Current process value
payload.error number Current error
payload.output number Control output
Node Status
The node displays real-time status:
  • Green dot: SP:22 PV:18 → 45.2% - Normal auto operation
  • Blue dot: MANUAL → 50.0% - Manual mode
  • Yellow dot: SP:22 PV:18 → 100% (clamped) - Output saturated
  • Yellow dot: SP:22 PV:18 → 45.2% (rate limited) - Rate limited
  • Cyan dot: SP:22 PV:18 → 45.2% (tracking) - Tracking mode active
  • Red dot: SP:22 PV:18 → 45.2% (interval!) - Max interval exceeded
Feed-Forward
Feed-forward compensates for disturbances before they cause errors.
Example: Room heating with outdoor temperature compensation
Without FF: Cold outside → Room cools → PID reacts → Valve opens
With FF:    Cold outside → Valve opens immediately → Room stays stable
The feed-forward value is added directly to the output:
output = PID(error) + ffGain × feedForward
Feed-forward does not affect the integrator - it's a parallel path.
msg.payload = roomTemperature;      // Process value
msg.feedForward = outsideTemp - 20; // Disturbance (deviation from 20°C)
Cascade Control (Tracking Mode)
Cascade control uses two PID controllers in series. The outer (master) loop controls the setpoint of the inner (slave) loop.
Problem without Tracking: When the inner loop saturates (valve at 100%), the outer loop's integrator keeps winding up, causing massive overshoot when saturation ends.
Solution with Tracking: Feed the inner loop's output back to the outer loop via msg.trackingValue. This forces the outer integrator to follow the actual output, preventing windup.
[Outer PID] ────setpoint────→ [Inner PID] ───→ Valve
      └─── msg.trackingValue ──────┘
Cascade Wiring Example
// Function node between Inner PID and Outer PID
// Sends inner output back to outer as tracking value
msg.trackingValue = msg.payload;  // Inner PID output
msg.payload = roomTemperature;    // Process value for outer PID
This is the same approach used by industrial controllers like Siemens FB41 (CONT_C) and Honeywell PID88.
Anti-Windup
Uses conditional integration: The integral only accumulates when it won't drive the output further into saturation. This prevents windup before it happens, rather than correcting it after.
The integrator is limited to ±(outputSpan/Ki) to prevent extreme values during long saturation periods. This ensures fast recovery when the process returns to normal range - no more waiting for a huge integral to wind down.
Bumpless Transfer
When switching from manual to auto mode, the integral term is pre-loaded so the output continues smoothly from the current manual value.
Safety Features
  • NaN/Infinity Protection - If output becomes NaN or Infinity, it freezes to the last valid output and back-calculates the integrator to maintain consistency
  • Feed-Forward Limiting - FF is clamped to ±outputSpan to prevent runaway output from extreme FF values
  • Tracking NaN Guard - Invalid tracking input (e.g. "abc") falls back to normal integration instead of freezing the integrator
  • Reset Restores Defaults - Reset command also restores the configured default setpoint
Centered Band (DDC-Style)
When enabled, output is 50% at setpoint:
  • Below setpoint → output > 50% (more heating)
  • Above setpoint → output < 50% (less heating)
Works with any output range (0-100, 0-10V, 4-20mA).
Example Flows
Basic Temperature Control
  "type": "pid-controller",
  "name": "Heater Control",
  "setpoint": 22,
  "Kp": 2,
  "Ti": 120,
  "Td": 30,
  "outMin": 0,
  "outMax": 100
Cooling Control (Reverse Acting)
  "name": "Chiller Control",
  "setpoint": 7,
  "Kp": 1.5,
  "Ti": 180,
  "reverseActing": true
Feed-Forward with Outdoor Temperature
// Function node before PID
msg.feedForward = (20 - outsideTemperature) * 0.5; // Scale factor
Tuning Tips
Ziegler-Nichols Method
  1. Set Ti = 0, Td = 0
  2. Increase Kp until oscillation occurs (Ku)
  3. Measure oscillation period (Tu)
  4. Set parameters:
    • P only: Kp = 0.5 × Ku
    • PI: Kp = 0.45 × Ku, Ti = Tu / 1.2
    • PID: Kp = 0.6 × Ku, Ti = Tu / 2, Td = Tu / 8
General Guidelines
  • Start with P only (Ti = 0, Td = 0)
  • Increase Kp until response is acceptable but not oscillating
  • Add I (reduce Ti) to eliminate steady-state error
  • Add D (increase Td) to reduce overshoot (use sparingly)
MIT
Author
sr.rpo - Building automation PID controller for Node-RED.
Version: 0.3.2
Updated 7 months, 3 weeks ago
214 in the last week
  • pid-controller
  • pid
  • controller
  • hvac
  • automation
  • isa
  • building-automation
  • process-control
  • cascade
  • tracking