Water Utility Complete Example
The system consists of two pumps and two tanks. The first pump pumps water from a well into the first tank, the second pump transfers water from the first to the second tank. This setup consists of four different locations; each has a Modbus RTUs or PLCs. The core of this SCADA system will be Node-Red which will read values from the tanks, start and stop pumps, provide alarming, and an HMI.
The Water Well / Transfer Pump Dashboard group shows the pump mode and status, as well as toggle buttons to turn them on and off. Tank level setpoints can be modified to change when the pump automatically starts and stops when in automatic mode. When in manual mode the pump can be started and stopped by hand.
The tank group has a line trend and bar chart trend to easily view the level and history of the level. Alarm set points are automatically set to be +15 and -15 around the pump start and stop set points, this could easily be modified to work differently. Finally there is a text alarm status that shows if the alarm is High, Low, or Clear. A text to speech node also announces the alarm status.
Nodes used: node-red-dashboard node-red-contrib-modbus
[{"id":"fcc84f3d.be1f6","type":"modbus-read","z":"bbb5a507.9eeaf8","name":"Read Holding Registers","showStatusActivities":false,"showErrors":false,"unitid":"1","dataType":"HoldingRegister","adr":"1","quantity":"6","rate":"500","rateUnit":"ms","server":"4412ae43.cdf648","x":165.1666717529297,"y":271.0000114440918,"wires":[[],["660bb503.b22aec"]]},{"id":"660bb503.b22aec","type":"function","z":"bbb5a507.9eeaf8","name":" Decode array","func":"//   The message returned from the read node is an\n// array as there could be multiple registers returned\n//   This reads the first value in the array.\ntank1Level = msg.payload.data[0]\ntank2Level = msg.payload.data[1]\ntank1Start = msg.payload.data[2]\ntank1Stop = msg.payload.data[3]\ntank2Start = msg.payload.data[4]\ntank2Stop = msg.payload.data[5]\n\nglobal.set(\"tank1Level\",tank1Level);\nglobal.set(\"tank2Level\",tank2Level);\nglobal.set(\"tank1Start\",tank1Start);\nglobal.set(\"tank1Stop\",tank1Stop);\nglobal.set(\"tank2Start\",tank2Start);\nglobal.set(\"tank2Stop\",tank2Stop);\n\ntank1HStp = (tank1Start - 15);\ntank1LStp = (tank1Stop + 15);\ntank2HStp = (tank1Start - 15);\ntank2LStp = (tank1Stop + 15);\n\nvar msg1 = { payload:tank1Level};\nvar msg2 = { payload:tank2Level};\nvar msg3 = { payload:tank1Start};\nvar msg4 = { payload:tank1Stop};\nvar msg5 = { payload:tank2Start};\nvar msg6 = { payload:tank2Stop};\nvar msg7 = { payload:tank1HStp};\nvar msg8 = { payload:tank1LStp};\nvar msg9 = { payload:tank2HStp};\nvar msg10 = { payload:tank2LStp};\n\n\n\n\nreturn [ msg1, msg2, msg3, msg4, msg5, msg6, msg7, msg8, msg9, msg10 ];\n","outputs":"10","noerr":0,"x":189.95352172851562,"y":392.7841606140137,"wires":[["49c3c886.f87b8","55a1e5af.309f4c","e3a629eb.ea149","130b2744.d7a7e9"],["a220c3a8.9f661","ba9b90ce.1265f","52d386d.840acf8","f4f81b9e.9ad468"],["143d5853.9a45"],["c4027384.f6e86"],["d7218949.295b28"],["50816a10.d0b244"],["560d158e.ab437c"],["4fb126cd.3aa7d"],["b1be0261.faeee8"],["b849217b.86a418"]]},{"id":"720b3e7.a7278c","type":"modbus-server","z":"bbb5a507.9eeaf8","name":"Modbus Server","logEnabled":false,"serverPort":"502","responseDelay":100,"delayUnit":"ms","coilsBufferSize":1024,"holdingBufferSize":1024,"inputBufferSize":1024,"x":322.16668701171875,"y":1242.000099658966,"wires":[["22edeef9.fe580a"],["22edeef9.fe580a"],["22edeef9.fe580a"]]},{"id":"22edeef9.fe580a","type":"debug","z":"bbb5a507.9eeaf8","name":"","active":true,"console":"false","complete":"false","x":546.1666870117188,"y":1242.000099658966,"wires":[]},{"id":"2f70edf9.23ebb2","type":"inject","z":"bbb5a507.9eeaf8","name":"","topic":"","payload":"","payloadType":"date","repeat":"","crontab":"","once":false,"x":133.16668701171875,"y":1242.000099658966,"wires":[["720b3e7.a7278c"]]},{"id":"89dc5d01.48f748","type":"comment","z":"bbb5a507.9eeaf8","name":"Modbus Slave sim device","info":"","x":161.86669731140137,"y":1199.0001020431519,"wires":[]},{"id":"55a1e5af.309f4c","type":"ui_chart","z":"bbb5a507.9eeaf8","name":"Bar Chart","group":"9bd788a1.b5bb98","order":3,"width":"2","height":"4","label":"","chartType":"bar","legend":"false","xformat":"HH:mm:ss","interpolate":"linear","nodata":"","ymin":"0","ymax":"240","removeOlder":"10","removeOlderPoints":"","removeOlderUnit":"60","cutout":0,"colors":["#1f77b4","#aec7e8","#ff7f0e","#2ca02c","#98df8a","#d62728","#ff9896","#9467bd","#c5b0d5"],"x":512.8667678833008,"y":157.6000361442566,"wires":[[],[]]},{"id":"49c3c886.f87b8","type":"ui_text","z":"bbb5a507.9eeaf8","group":"9bd788a1.b5bb98","order":1,"width":0,"height":0,"name":"","label":"Tank 1 Level","format":"{{msg.payload}}","layout":"row-spread","x":521.8667678833008,"y":123.39996290206909,"wires":[]},{"id":"ba9b90ce.1265f","type":"ui_chart","z":"bbb5a507.9eeaf8","name":"Trend","group":"7b6e0d6c.f51904","order":2,"width":"3","height":"4","label":"","chartType":"line","legend":"false","xformat":"HH:mm:ss","interpolate":"linear","nodata":"","ymin":"0","ymax":"240","removeOlder":"3","removeOlderPoints":"","removeOlderUnit":"60","cutout":0,"colors":["#1f77b4","#aec7e8","#ff7f0e","#2ca02c","#98df8a","#d62728","#ff9896","#9467bd","#c5b0d5"],"x":502.8667678833008,"y":303.866614818573,"wires":[[],[]]},{"id":"a220c3a8.9f661","type":"ui_text","z":"bbb5a507.9eeaf8","group":"7b6e0d6c.f51904","order":1,"width":0,"height":0,"name":"","label":"Tank 2 Level","format":"{{msg.payload}}","layout":"row-spread","x":520.8667678833008,"y":236.6665415763855,"wires":[]},{"id":"4f5ef788.4e5fd8","type":"ui_text","z":"bbb5a507.9eeaf8","group":"912c5aef.7152f","order":1,"width":"3","height":"1","name":"","label":"Mode","format":"{{msg.payload}}","layout":"row-left","x":508.20019149780273,"y":686.399896144867,"wires":[]},{"id":"77748bba.cd8934","type":"ui_switch","z":"bbb5a507.9eeaf8","name":"","label":"Run","group":"912c5aef.7152f","order":4,"width":"3","height":"1","passthru":false,"decouple":"false","topic":"","style":"","onvalue":"true","onvalueType":"bool","onicon":"","oncolor":"","offvalue":"false","offvalueType":"bool","officon":"","offcolor":"","x":676.3998794555664,"y":410.8333811759949,"wires":[["a9f807ab.445d4"]]},{"id":"e0707a69.906d2","type":"debug","z":"bbb5a507.9eeaf8","name":"","active":false,"console":"false","complete":"false","x":1134.115837097168,"y":543.7337260246277,"wires":[]},{"id":"65e81333.7ce74c","type":"function","z":"bbb5a507.9eeaf8","name":"pump 1 simulator","func":"//   The message returned from the read node is an\n// array as there could be multiple registers returned\n//   This reads the first value in the array.\nvar tankLevel = global.get(\"tank1Level\");\nvar pumpStatus = global.get(\"pump1Status\");\nvar pump2Status = global.get(\"pump2Status\");\n\n\nif (pumpStatus === true && tankLevel < 240)\n{\n    if (pump2Status === true) \n    {\n        tankLevel = tankLevel + 1; \n        msg.payload = { value: tankLevel, \n        'fc': 6,\n        'unitid': 1, \n        'address': 1,\n        'quantity': 1 } \n        return msg\n    }\n    else\n    {\n        tankLevel = tankLevel + 6; \n        msg.payload = { value: tankLevel, \n        'fc': 6,\n        'unitid': 1, \n        'address': 1,\n        'quantity': 1 } \n        return msg\n    }\n}   \nelse if (pumpStatus === false && tankLevel > 4)\n{\n    if (pump2Status === true) \n    {\n        tankLevel = tankLevel + -6; \n        msg.payload = { value: tankLevel, \n        'fc': 6,\n        'unitid': 1, \n        'address': 1,\n        'quantity': 1 } \n        return msg \n    }\n    else\n    {\n        tankLevel = tankLevel + -2; \n        msg.payload = { value: tankLevel, \n        'fc': 6,\n        'unitid': 1, \n        'address': 1,\n        'quantity': 1 } \n        return msg \n    }\n    \n}\n","outputs":1,"noerr":0,"x":299.23326110839844,"y":1080.3332905769348,"wires":[["1b900cb2.8100d3"]]},{"id":"d160b042.20e8d","type":"inject","z":"bbb5a507.9eeaf8","name":"","topic":"","payload":"true","payloadType":"bool","repeat":"1","crontab":"","once":false,"x":122.39996337890625,"y":1095.9999165534973,"wires":[["65e81333.7ce74c","ee4bba80.dd2c1"]]},{"id":"50db2e50.99014","type":"ui_switch","z":"bbb5a507.9eeaf8","name":"","label":"Mode","group":"912c5aef.7152f","order":3,"width":"3","height":"1","passthru":false,"decouple":"true","topic":"","style":"","onvalue":"true","onvalueType":"bool","onicon":"","oncolor":"","offvalue":"false","offvalueType":"bool","officon":"","offcolor":"","x":675.566535949707,"y":373.3334422111511,"wires":[["59532462.61a4f4"]]},{"id":"e0574d1f.547848","type":"modbus-flex-write","z":"bbb5a507.9eeaf8","name":"","showStatusActivities":false,"showErrors":false,"server":"4412ae43.cdf648","x":1119.3998947143555,"y":500.3335795402527,"wires":[[],["e0707a69.906d2"]]},{"id":"a9f807ab.445d4","type":"function","z":"bbb5a507.9eeaf8","name":"Coil 2","func":"msg.payload = { value: msg.payload, \n'fc': 5,\n'unitid': 1, \n'address': 2,\n'quantity': 1 } \nreturn msg","outputs":1,"noerr":0,"x":805.3999099731445,"y":411.0001902580261,"wires":[["e0574d1f.547848"]]},{"id":"59532462.61a4f4","type":"function","z":"bbb5a507.9eeaf8","name":"Coil 1","func":"msg.payload = { value: msg.payload, \n'fc': 5,\n'unitid': 1, \n'address': 1,\n'quantity': 1 } \nreturn msg","outputs":1,"noerr":0,"x":805.566535949707,"y":373.3335032463074,"wires":[["e0574d1f.547848"]]},{"id":"771f5b0.f3bdca4","type":"ui_switch","z":"bbb5a507.9eeaf8","name":"","label":"Run","group":"4025c129.a588a8","order":4,"width":"3","height":"1","passthru":false,"decouple":"true","topic":"","style":"","onvalue":"true","onvalueType":"bool","onicon":"","oncolor":"","offvalue":"false","offvalueType":"bool","officon":"","offcolor":"","x":672.566520690918,"y":573.6669383049011,"wires":[["3a9de7f6.babdb"]]},{"id":"6a49013c.a9316","type":"ui_switch","z":"bbb5a507.9eeaf8","name":"","label":"Mode","group":"4025c129.a588a8","order":3,"width":"3","height":"1","passthru":false,"decouple":"true","topic":"","style":"","onvalue":"true","onvalueType":"bool","onicon":"","oncolor":"","offvalue":"false","offvalueType":"bool","officon":"","offcolor":"","x":671.7331771850586,"y":536.1669993400574,"wires":[["acc8b845.c10238"]]},{"id":"3a9de7f6.babdb","type":"function","z":"bbb5a507.9eeaf8","name":"Coil 3","func":"msg.payload = { value: msg.payload, \n'fc': 5,\n'unitid': 1, \n'address': 4,\n'quantity': 1 } \nreturn msg","outputs":1,"noerr":0,"x":802.5665512084961,"y":573.8337473869324,"wires":[["e0574d1f.547848"]]},{"id":"acc8b845.c10238","type":"function","z":"bbb5a507.9eeaf8","name":"Coil 3","func":"msg.payload = { value: msg.payload, \n'fc': 5,\n'unitid': 1, \n'address': 3,\n'quantity': 1 } \nreturn msg","outputs":1,"noerr":0,"x":801.7331771850586,"y":536.1671214103699,"wires":[["e0574d1f.547848"]]},{"id":"6c0935f1.938834","type":"modbus-read","z":"bbb5a507.9eeaf8","name":"Read Coils","showStatusActivities":false,"showErrors":false,"unitid":"1","dataType":"Coil","adr":"1","quantity":"6","rate":"500","rateUnit":"ms","server":"4412ae43.cdf648","x":131.90003967285156,"y":580.3333992958069,"wires":[[],["a088702f.37e718"]]},{"id":"a088702f.37e718","type":"function","z":"bbb5a507.9eeaf8","name":" Decode array","func":"// get the modbus values from the array\npump1Mode = msg.payload.data[0]\npump1Status = msg.payload.data[1]\npump2Mode = msg.payload.data[2]\npump2Status = msg.payload.data[3]\n\n//set global context variables for the simulator\nglobal.set(\"pump1Mode\",pump1Mode);\nglobal.set(\"pump1Status\",pump1Status);\nglobal.set(\"pump2Mode\",pump2Mode);\nglobal.set(\"pump2Status\",pump2Status);\n\n//Set up text for the statuses\nif (pump1Mode)\n    {\n    p1MText = 'Auto';\n    }\nelse\n    {\n    p1MText = 'Manual';\n    }\n    \nif (pump1Status)\n    {\n    p1SText = 'Running';\n    }\nelse\n    {\n    p1SText = 'Stopped';\n    }\n    \nif (pump2Mode)\n    {\n    p2MText = 'Auto';\n    }\nelse\n    {\n    p2MText = 'Manual';\n    }\n    \nif (pump2Status)\n    {\n    p2SText = 'Running';\n    }\nelse\n    {\n    p2SText = 'Stopped';\n    }\n    \n//set up the outgoing messages\nvar msg1 = { payload:p1MText};\nvar msg2 = { payload:p1SText};\nvar msg3 = { payload:p2MText};\nvar msg4 = { payload:p2SText};\nvar msg5 = { payload:pump1Mode};\nvar msg6 = { payload:pump1Status};\nvar msg7 = { payload:pump2Mode};\nvar msg8 = { payload:pump2Status};\n\n\n\nreturn [ msg1, msg2, msg3, msg4, msg5, msg6, msg7, msg8 ];\n","outputs":"8","noerr":0,"x":176.68687438964844,"y":690.1175036430359,"wires":[["4f5ef788.4e5fd8"],["44fdb46d.e824e4"],["ffe7dba5.bf9d9"],["1757e22b.08ba1e"],["50db2e50.99014"],["77748bba.cd8934"],["6a49013c.a9316"],["771f5b0.f3bdca4"]]},{"id":"ffe7dba5.bf9d9","type":"ui_text","z":"bbb5a507.9eeaf8","group":"4025c129.a588a8","order":1,"width":"3","height":"1","name":"","label":"Mode","format":"{{msg.payload}}","layout":"row-spread","x":506.5668296813965,"y":759.999993801117,"wires":[]},{"id":"44fdb46d.e824e4","type":"ui_text","z":"bbb5a507.9eeaf8","group":"912c5aef.7152f","order":2,"width":"3","height":"1","name":"","label":"Status","format":"{{msg.payload}}","layout":"row-left","x":507.5668296813965,"y":722.999993801117,"wires":[]},{"id":"1757e22b.08ba1e","type":"ui_text","z":"bbb5a507.9eeaf8","group":"4025c129.a588a8","order":2,"width":"3","height":"1","name":"","label":"Status","format":"{{msg.payload}}","layout":"row-spread","x":507.5668296813965,"y":797.999993801117,"wires":[]},{"id":"8e10b238.58359","type":"comment","z":"bbb5a507.9eeaf8","name":"Level Simulator","info":"","x":146.3999481201172,"y":1042.9999775886536,"wires":[]},{"id":"4df0fc34.f79e34","type":"debug","z":"bbb5a507.9eeaf8","name":"","active":false,"console":"false","complete":"false","x":939.233341217041,"y":1047.666642665863,"wires":[]},{"id":"1b900cb2.8100d3","type":"modbus-flex-write","z":"bbb5a507.9eeaf8","name":"","showStatusActivities":false,"showErrors":true,"server":"4412ae43.cdf648","x":731.5174331665039,"y":1041.266496181488,"wires":[[],["4df0fc34.f79e34"]]},{"id":"66d4f093.f28ac","type":"function","z":"bbb5a507.9eeaf8","name":"pump 2 simulator","func":"//   The message returned from the read node is an\n// array as there could be multiple registers returned\n//   This reads the first value in the array.\nvar tank1Level = global.get(\"tank1Level\");\nvar tankLevel = global.get(\"tank2Level\");\nvar pumpStatus = global.get(\"pump2Status\");\n\n\nif (pumpStatus === true && tankLevel < 240 && tank1Level > 3)\n{\n    tankLevel = tankLevel + 6; \n    msg.payload = { value: tankLevel, \n    'fc': 6,\n    'unitid': 1, \n    'address': 2,\n    'quantity': 1 } \n    return msg \n}   \nelse if (pumpStatus === false && tankLevel > 0)\n{\n    tankLevel = tankLevel + -2; \n    msg.payload = { value: tankLevel, \n    'fc': 6,\n    'unitid': 1, \n    'address': 2,\n    'quantity': 1 } \n    return msg \n}","outputs":"1","noerr":0,"x":473.2332763671875,"y":1119.3331379890442,"wires":[["1b900cb2.8100d3"]]},{"id":"e3a629eb.ea149","type":"ui_chart","z":"bbb5a507.9eeaf8","name":"Trend","group":"9bd788a1.b5bb98","order":2,"width":"3","height":"4","label":"","chartType":"line","legend":"false","xformat":"HH:mm:ss","interpolate":"linear","nodata":"","ymin":"0","ymax":"240","removeOlder":"3","removeOlderPoints":"","removeOlderUnit":"60","cutout":0,"colors":["#1f77b4","#aec7e8","#ff7f0e","#2ca02c","#98df8a","#d62728","#ff9896","#9467bd","#c5b0d5"],"x":504.23340606689453,"y":191.3333125114441,"wires":[[],[]]},{"id":"52d386d.840acf8","type":"ui_chart","z":"bbb5a507.9eeaf8","name":"Bar Chart","group":"7b6e0d6c.f51904","order":3,"width":"2","height":"4","label":"","chartType":"bar","legend":"false","xformat":"HH:mm:ss","interpolate":"linear","nodata":"","ymin":"0","ymax":"240","removeOlder":"10","removeOlderPoints":"","removeOlderUnit":"60","cutout":0,"colors":["#1f77b4","#aec7e8","#ff7f0e","#2ca02c","#98df8a","#d62728","#ff9896","#9467bd","#c5b0d5"],"x":512.2334060668945,"y":270.3333201408386,"wires":[[],[]]},{"id":"143d5853.9a45","type":"ui_numeric","z":"bbb5a507.9eeaf8","name":"","label":"Start Setpoint","group":"912c5aef.7152f","order":5,"width":"0","height":"0","passthru":false,"topic":"","format":"{{value}}","min":"0","max":"230","step":1,"x":706.3999099731445,"y":445.666663646698,"wires":[["9697b148.83f408"]]},{"id":"c4027384.f6e86","type":"ui_numeric","z":"bbb5a507.9eeaf8","name":"","label":"Stop Setpoint","group":"912c5aef.7152f","order":6,"width":"0","height":"0","passthru":false,"topic":"","format":"{{value}}","min":"10","max":"240","step":1,"x":707.2332382202148,"y":482.0000376701355,"wires":[["4e695501.48ccac"]]},{"id":"d7218949.295b28","type":"ui_numeric","z":"bbb5a507.9eeaf8","name":"","label":"Start Setpoint","group":"4025c129.a588a8","order":5,"width":"0","height":"0","passthru":false,"topic":"","format":"{{value}}","min":"0","max":"230","step":1,"x":701.2332382202148,"y":610.3333506584167,"wires":[["ef212684.39b1f"]]},{"id":"50816a10.d0b244","type":"ui_numeric","z":"bbb5a507.9eeaf8","name":"","label":"Stop Setpoint","group":"4025c129.a588a8","order":6,"width":"0","height":"0","passthru":false,"topic":"","format":"{{value}}","min":"10","max":"240","step":1,"x":702.0665512084961,"y":646.666663646698,"wires":[["218b0e82.825eb2"]]},{"id":"9697b148.83f408","type":"function","z":"bbb5a507.9eeaf8","name":"Hld 3","func":"msg.payload = { value: msg.payload, \n'fc': 6,\n'unitid': 1, \n'address': 3,\n'quantity': 1 } \nreturn msg","outputs":1,"noerr":0,"x":854.2332229614258,"y":446.3333811759949,"wires":[["e0574d1f.547848"]]},{"id":"4e695501.48ccac","type":"function","z":"bbb5a507.9eeaf8","name":"Hld 4","func":"msg.payload = { value: msg.payload, \n'fc': 6,\n'unitid': 1, \n'address': 4,\n'quantity': 1 } \nreturn msg","outputs":1,"noerr":0,"x":855.2332229614258,"y":482.33335065841675,"wires":[["e0574d1f.547848"]]},{"id":"ef212684.39b1f","type":"function","z":"bbb5a507.9eeaf8","name":"Hld 5","func":"msg.payload = { value: msg.payload, \n'fc': 6,\n'unitid': 1, \n'address': 5,\n'quantity': 1 } \nreturn msg","outputs":1,"noerr":0,"x":851.2332229614258,"y":610.3333506584167,"wires":[["e0574d1f.547848"]]},{"id":"218b0e82.825eb2","type":"function","z":"bbb5a507.9eeaf8","name":"Hld 6","func":"msg.payload = { value: msg.payload, \n'fc': 6,\n'unitid': 1, \n'address': 6,\n'quantity': 1 } \nreturn msg","outputs":1,"noerr":0,"x":852.2332229614258,"y":646.3333201408386,"wires":[["e0574d1f.547848"]]},{"id":"ee4bba80.dd2c1","type":"delay","z":"bbb5a507.9eeaf8","name":"","pauseType":"delay","timeout":"300","timeoutUnits":"milliseconds","rate":"1","nbRateUnits":"1","rateUnits":"second","randomFirst":"1","randomLast":"5","randomUnits":"seconds","drop":false,"x":279.3999328613281,"y":1119.999855518341,"wires":[["66d4f093.f28ac"]]},{"id":"f72dd87.4a3c7a8","type":"comment","z":"bbb5a507.9eeaf8","name":"Automatic Logic","info":"","x":707.2333297729492,"y":728.3332133293152,"wires":[]},{"id":"e13b9450.9ce78","type":"inject","z":"bbb5a507.9eeaf8","name":"","topic":"","payload":"true","payloadType":"bool","repeat":"1","crontab":"","once":false,"x":674.2333297729492,"y":779.3330912590027,"wires":[["d0e0405.d8a6cc","46e6edbe.12d92c"]]},{"id":"d0e0405.d8a6cc","type":"function","z":"bbb5a507.9eeaf8","name":"pump 1 auto","func":"//   The message returned from the read node is an\n// array as there could be multiple registers returned\n//   This reads the first value in the array.\nvar tankLevel = global.get(\"tank1Level\");\nvar pumpMode = global.get(\"pump1Mode\");\nvar pumpStatus = global.get(\"pump1Status\");\nvar tankStart = global.get(\"tank1Start\");\nvar tankStop = global.get(\"tank1Stop\");\n\nif (pumpMode === true && pumpStatus === false && tankLevel <= tankStart)\n{\n    msg.payload = { value: true, \n    'fc': 5,\n    'unitid': 1, \n    'address': 2,\n    'quantity': 1 } \n    return msg\n}\nelse if (pumpMode === true && pumpStatus === true && tankLevel >= tankStop)\n{\n    msg.payload = { value: false, \n    'fc': 5,\n    'unitid': 1, \n    'address': 2,\n    'quantity': 1 } \n    return msg\n}","outputs":1,"noerr":0,"x":842.2333297729492,"y":761.3330302238464,"wires":[["e0574d1f.547848"]]},{"id":"46e6edbe.12d92c","type":"function","z":"bbb5a507.9eeaf8","name":"pump 2 auto","func":"//   The message returned from the read node is an\n// array as there could be multiple registers returned\n//   This reads the first value in the array.\nvar tankLevel = global.get(\"tank2Level\");\nvar pumpMode = global.get(\"pump2Mode\");\nvar pumpStatus = global.get(\"pump2Status\");\nvar tankStart = global.get(\"tank2Start\");\nvar tankStop = global.get(\"tank2Stop\");\n\n\nif (pumpMode === true && pumpStatus === false && tankLevel <= tankStart)\n{\n    msg.payload = { value: true, \n    'fc': 5,\n    'unitid': 1, \n    'address': 4,\n    'quantity': 1 } \n    return msg\n}\nelse if (pumpMode === true && pumpStatus === true && tankLevel >= tankStop)\n{\n    msg.payload = { value: false, \n    'fc': 5,\n    'unitid': 1, \n    'address': 4,\n    'quantity': 1 } \n    return msg\n}","outputs":1,"noerr":0,"x":843.2333297729492,"y":796.6665263175964,"wires":[["e0574d1f.547848"]]},{"id":"3ef0307a.718e88","type":"inject","z":"bbb5a507.9eeaf8","name":"","topic":"","payload":"true","payloadType":"bool","repeat":"","crontab":"","once":true,"x":122.4000244140625,"y":938.6667256355286,"wires":[["10682cef.4f3be3","a33c255f.ab5138"]]},{"id":"97d4d6d6.f6064","type":"function","z":"bbb5a507.9eeaf8","name":"Startup Values","func":"msg.payload = { value:[false, false, false, false], \n'fc': 15, \n'unitid': 1, \n'address': 0, \n'quantity': 4 } \nreturn msg","outputs":1,"noerr":0,"x":463.2333221435547,"y":939.3334126472473,"wires":[["1b900cb2.8100d3"]]},{"id":"10682cef.4f3be3","type":"delay","z":"bbb5a507.9eeaf8","name":"","pauseType":"delay","timeout":"5","timeoutUnits":"seconds","rate":"1","nbRateUnits":"1","rateUnits":"second","randomFirst":"1","randomLast":"5","randomUnits":"seconds","drop":false,"x":281.40000915527344,"y":939.0000996589661,"wires":[["97d4d6d6.f6064"]]},{"id":"2d547ec5.a27d52","type":"function","z":"bbb5a507.9eeaf8","name":"Startup Values","func":"msg.payload = { value:[180,180,150,200,150,200], \n'fc': 16, \n'unitid': 1, \n'address': 1, \n'quantity': 6 } \nreturn msg","outputs":1,"noerr":0,"x":463.2333221435547,"y":975.3334126472473,"wires":[["1b900cb2.8100d3"]]},{"id":"a33c255f.ab5138","type":"delay","z":"bbb5a507.9eeaf8","name":"","pauseType":"delay","timeout":"6","timeoutUnits":"seconds","rate":"1","nbRateUnits":"1","rateUnits":"second","randomFirst":"1","randomLast":"5","randomUnits":"seconds","drop":false,"x":281.40000915527344,"y":975.0000996589661,"wires":[["2d547ec5.a27d52"]]},{"id":"55c22273.da3ae4","type":"comment","z":"bbb5a507.9eeaf8","name":"Read Me for Register Info","info":"Coils\n1 Pump 1 Mode\n2 pump 1 Run Status\n3 Pump 2 Mode\n4 Pump 2 Run Status\n\nHolding Registers\n40001 Tank 1 Level\n40002 Tank 1 Start Setpoint\n40003 Tank 1 Stop Setpoint\n40004 Tank 2 Level\n40005 Tank 2 Start Setpoint\n40006 Tank 2 Stop Setpoint\n","x":164.7833709716797,"y":219.88337326049805,"wires":[]},{"id":"56417c7f.53490c","type":"comment","z":"bbb5a507.9eeaf8","name":"Modbus read, write and dashboard icons","info":"\n","x":217.06671142578125,"y":182.16669845581055,"wires":[]},{"id":"39a0ce33.43792a","type":"comment","z":"bbb5a507.9eeaf8","name":"Startup Sim Values","info":"","x":154.16668701171875,"y":905.5334248542786,"wires":[]},{"id":"23512bab.734fac","type":"ui_text","z":"bbb5a507.9eeaf8","group":"9bd788a1.b5bb98","order":6,"width":0,"height":0,"name":"","label":"Tank 1","format":"{{msg.payload}}","layout":"row-spread","x":937.4001960754395,"y":138.50008916854858,"wires":[]},{"id":"130b2744.d7a7e9","type":"function","z":"bbb5a507.9eeaf8","name":"notification","func":"lvl = msg.payload\nmsg.topic = 'Tank 1 Alarm';\nvar tank1Alarm = global.get(\"tank1Alarm\");\nvar tank1Start = global.get(\"tank1Start\");\nvar tank1Stop = global.get(\"tank1Stop\");\n    \nif (lvl > (tank1Stop + 15))\n{\n    msg.payload = 'Tank 1 Level High Alarm';\n}\nelse if (lvl < (tank1Start - 15))\n{\n    msg.payload = 'Tank 1 Level Low Alarm'; \n}\nelse\n{\n      msg.payload = 'Tank 1 Alarm Clear';  \n}\n\nif (msg.payload != tank1Alarm)\n{\n    global.set(\"tank1Alarm\",msg.payload);\n    return msg;\n}","outputs":1,"noerr":0,"x":763.6501350402832,"y":138.96670293807983,"wires":[["23512bab.734fac","389aabdc.4c980c"]]},{"id":"1c93a739.018941","type":"ui_audio","z":"bbb5a507.9eeaf8","name":"","group":"34a91890.9fc56","voice":"1","always":"","x":1081.9003067016602,"y":101.16671657562256,"wires":[]},{"id":"6e205664.eb0258","type":"ui_text","z":"bbb5a507.9eeaf8","group":"7b6e0d6c.f51904","order":6,"width":0,"height":0,"name":"","label":"Tank 2","format":"{{msg.payload}}","layout":"row-spread","x":937.9001541137695,"y":171.5667281150818,"wires":[]},{"id":"f4f81b9e.9ad468","type":"function","z":"bbb5a507.9eeaf8","name":"notification","func":"lvl = msg.payload\nmsg.topic = 'Tank 2 Alarm';\nvar tank2Alarm = global.get(\"tank2Alarm\");\nvar tank2Start = global.get(\"tank2Start\");\nvar tank2Stop = global.get(\"tank2Stop\");\n    \nif (lvl > (tank2Stop + 15))    \n{\n    msg.payload = 'Tank 2 Level High Alarm';\n}\nelse if (lvl < (tank2Start - 15))\n{\n    msg.payload = 'Tank 2 Level Low Alarm'; \n}\nelse\n{\n      msg.payload = 'Tank 2 Alarm Clear';  \n}\n\nif (msg.payload != tank2Alarm)\n{\n    global.set(\"tank2Alarm\",msg.payload);\n    return msg;\n}","outputs":1,"noerr":0,"x":762.1500930786133,"y":172.03334188461304,"wires":[["6e205664.eb0258","389aabdc.4c980c"]]},{"id":"560d158e.ab437c","type":"ui_text","z":"bbb5a507.9eeaf8","group":"9bd788a1.b5bb98","order":4,"width":"3","height":"1","name":"","label":"Low Setpt","format":"{{msg.payload}}","layout":"row-left","x":946.4002265930176,"y":205.00012731552124,"wires":[]},{"id":"4fb126cd.3aa7d","type":"ui_text","z":"bbb5a507.9eeaf8","group":"9bd788a1.b5bb98","order":5,"width":"3","height":"1","name":"","label":"High Stpt","format":"{{msg.payload}} ","layout":"row-left","x":945.5669441223145,"y":239.00012254714966,"wires":[]},{"id":"b1be0261.faeee8","type":"ui_text","z":"bbb5a507.9eeaf8","group":"7b6e0d6c.f51904","order":4,"width":"3","height":"1","name":"","label":"Low Stpt","format":"{{msg.payload}}","layout":"row-left","x":943.9002380371094,"y":273.00009870529175,"wires":[]},{"id":"b849217b.86a418","type":"ui_text","z":"bbb5a507.9eeaf8","group":"7b6e0d6c.f51904","order":5,"width":"3","height":"1","name":"","label":"High Stpt","format":"{{msg.payload}} ","layout":"row-left","x":943.0668334960938,"y":307.0000567436218,"wires":[]},{"id":"61603830.6a2208","type":"comment","z":"bbb5a507.9eeaf8","name":"Alarming","info":"\n","x":717.900276184082,"y":80.00004768371582,"wires":[]},{"id":"696d50f6.b9a7f","type":"function","z":"bbb5a507.9eeaf8","name":"","func":"\nif (msg.payload == 1)\n{\n    global.set(\"enable\", 1);\n   // return msg;\n}\nelse\n{\n    global.set(\"enable\", 0);     \n}\n\n","outputs":1,"noerr":0,"x":1072.166748046875,"y":63,"wires":[[]]},{"id":"1ef97daf.f77c42","type":"ui_switch","z":"bbb5a507.9eeaf8","name":"","label":"Enable Audio TTS","group":"34a91890.9fc56","order":0,"width":0,"height":0,"passthru":true,"decouple":"false","topic":"EnableBtn","style":"","onvalue":"1","onvalueType":"num","onicon":"","oncolor":"","offvalue":"0","offvalueType":"num","officon":"","offcolor":"","x":912.1668090820312,"y":63.09720230102539,"wires":[["696d50f6.b9a7f"]]},{"id":"389aabdc.4c980c","type":"function","z":"bbb5a507.9eeaf8","name":"","func":"var enable = global.get(\"enable\");\n\nif (enable == 1)\n{\n    return msg;\n}\n\n","outputs":1,"noerr":0,"x":950.1666564941406,"y":101.00002384185791,"wires":[["1c93a739.018941"]]},{"id":"4412ae43.cdf648","type":"modbus-client","z":"","name":"local","clienttype":"tcp","bufferCommands":true,"stateLogEnabled":false,"tcpHost":"127.0.0.1","tcpPort":"502","tcpType":"DEFAULT","serialPort":"/dev/ttyUSB","serialType":"RTU-BUFFERD","serialBaudrate":"9600","serialDatabits":"8","serialStopbits":"1","serialParity":"none","serialConnectionDelay":"100","unit_id":"1","commandDelay":"1","clientTimeout":"1000","reconnectTimeout":"2000"},{"id":"9bd788a1.b5bb98","type":"ui_group","z":"","name":"Tank 1","tab":"66634e5c.10174","order":2,"disp":true,"width":"6"},{"id":"7b6e0d6c.f51904","type":"ui_group","z":"","name":"Tank 2","tab":"66634e5c.10174","order":4,"disp":true,"width":"6"},{"id":"912c5aef.7152f","type":"ui_group","z":"","name":"Water Well","tab":"66634e5c.10174","order":1,"disp":true,"width":"6"},{"id":"4025c129.a588a8","type":"ui_group","z":"","name":"Transfer Pump","tab":"66634e5c.10174","order":3,"disp":true,"width":"6"},{"id":"34a91890.9fc56","type":"ui_group","z":"","name":"Alarming","tab":"66634e5c.10174","disp":true,"width":"6"},{"id":"66634e5c.10174","type":"ui_tab","z":"","name":"Water Utility","icon":"dashboard"}]
Created 9 years, 11 months ago
Rating: 4.25 4
  • comment (x7)
  • debug (x3)
  • delay (x3)
  • function (x20)
  • inject (x4)
  • modbus-client (x1)
  • modbus-flex-write (x2)
  • modbus-read (x2)
  • modbus-server (x1)
  • ui_audio (x1)
  • ui_chart (x4)
  • ui_group (x5)
  • ui_numeric (x4)
  • ui_switch (x5)
  • ui_text (x12)
  • Water
  • scada
  • freewave
  • complete
  • tutorial
  • modbus