node-red-contrib-pid-controller 0.1.4
A PID Loop control node
npm install node-red-contrib-pid-controller
PID Control Node
This node has 2 outputs, the first is for heating control, the second is for cooling control.
Both outputs provide a floating point value between 0 and 10.
Settings
The node takes the following configuration values:
  • Gain: The % gain to apply to the difference between the setpoint and input value
  • Ti: The time in seconds over which to apply the gain value
  • Dead Band: The +/- each side of the setpoint to consider the setpoint reached
  • Recalculation Time: The time in seconds between each calculation of values
  • Setpoint Topic: the topic a message should have to set the setpoint
  • Fire Topic: the topic a message should have to enable/disable Fire mode
  • Fixed Value Topic: the topic a message should have to enable/disable fixed output mode
  • Fixed Value: the value to output when in fixed mode, +ve for heating -ve for cooling
Operations
Before you can use the node you need to set the setpoint, to do this you need send a message with the setpoint value as the payload and a topic set to the Setpoint Topic configured in the editor UI.
Fire mode sets all outputs to 0. Fire mode is enabled by sending a message with a payload of false to and a topic equal to the Fire Topic. To disable Fire mode send a message with a payload of true and a topic equal to the Fire Topic
Hysteresis Node
This node gives a true output value when the input values are outside the deadband of the setpoint and a false when the setpoint is reached.
Version: 0.1.4
15 in the last week
  • PIDLoop
  • hysteresis